Missing winding 2

Status
Not open for further replies.

JAB1961

Industrial
Dec 21, 2004
6
I have a motor that is running on 3 ph 240 volt.
I went to switch it to 3 ph 480 and found it would not run.
After checking each winding I found from 1 to 4 is open.
I put it back to the 240 and it runs.
Why is this and what is it doing to this motor?
 
Replies continue below

Recommended for you

For 240 V, the windings are in parallel. For 480 V the windings are in series. So with 1-4 open, at 240 V one phase is "Half open" but the phase is still there. At 480 V the phase is open circuit and the motor won't start because it is "single phasing" (one phase not operating) (but it pulls a lot of current).
 
What Sreid explained is the reason the motor still spins while connected in parallel ( 240), however it does not mean it is 100% good, the phase currents must be unbalanced generating a considerable negative sequence which traduces in lower torque and rotor overheating.
 