I have a small residential building with sprinkler designed per NFPA #13R.
With the exception of a single sitting room all sprinklers outside the dwelling units are at 8'-0" but the sitting room (requires three sprinklers) has a vaulted ceiling that goes up to 13'-5" AFF and, since it is outside the dwelling unit, regular quick response sprinklers need to be used.
See image.
There is not a lintel between the vaulted ceiling sitting room and corridor... just an open passageway.
I don't think there is a problem mixing heads in this manner but I wanted to check here first.
Calculations? Three heads in the corridor (there are only three) and one or two in the sitting room?
TIA
With the exception of a single sitting room all sprinklers outside the dwelling units are at 8'-0" but the sitting room (requires three sprinklers) has a vaulted ceiling that goes up to 13'-5" AFF and, since it is outside the dwelling unit, regular quick response sprinklers need to be used.
See image.
There is not a lintel between the vaulted ceiling sitting room and corridor... just an open passageway.
I don't think there is a problem mixing heads in this manner but I wanted to check here first.
Calculations? Three heads in the corridor (there are only three) and one or two in the sitting room?