My first project as a rooky structural engineer has been to design a simple steel frame building. All of the beam-to-column connections are simple shear connections.
I am concerned that the eccentricity of loading for these columns may cause excessive moments to be induced in them. I'm using 5x5 square tubes with single plate shear connections. Thus, the eccentricity of load is about 5.5" (bolt line to CL).
Other engineers in my office do not concern themselves with the eccentricity of the load and do not treat the columns as beam - columns.
The potential for moment to be generated, especially if I consider the possibility of some bays being loaded while others are not (no counter balance), seems as though it should be investigated.
I calculate the moment induced by multiplying the load on the column by the 5.5" eccentricity. Is there some other way to view this situation that makes it acceptable to ignore the moment due to eccentricity?
I've been reading up on torsion and I've learned that the torsion induced by side loading a member is NOT equal to the joist reaction x eccentricity of load. One has to apporach it from a deformation compatibility standpoint. Maybe that could be the case here?
If anyone has any advice, it would be greatly appreciated.
I am concerned that the eccentricity of loading for these columns may cause excessive moments to be induced in them. I'm using 5x5 square tubes with single plate shear connections. Thus, the eccentricity of load is about 5.5" (bolt line to CL).
Other engineers in my office do not concern themselves with the eccentricity of the load and do not treat the columns as beam - columns.
The potential for moment to be generated, especially if I consider the possibility of some bays being loaded while others are not (no counter balance), seems as though it should be investigated.
I calculate the moment induced by multiplying the load on the column by the 5.5" eccentricity. Is there some other way to view this situation that makes it acceptable to ignore the moment due to eccentricity?
I've been reading up on torsion and I've learned that the torsion induced by side loading a member is NOT equal to the joist reaction x eccentricity of load. One has to apporach it from a deformation compatibility standpoint. Maybe that could be the case here?
If anyone has any advice, it would be greatly appreciated.