Modeling SC Current on Substation Transformer Secondary 1

Status
Not open for further replies.

tmaly1

Electrical
Oct 13, 2003
31
We know the Utility Available Fault Current on the 115 kV Substation Side (@100 MVA base), also, source impedances are known as well as the Substation Transformer Z% (%8).

How do I Calculate the Fault Current on 13.2kV Secondary Side of the Substation Transformer (115/13.2, 21 MVA, %Z=8)

Thanks in advance for your help and time
 
Replies continue below

Recommended for you

This is no place for home work !!!!

Read up the text books or IEEE "Buff" or "Red" Book.
 
hint: try Ohm's Law


Bung
Life is non-linear...
 
Comment: Everyone is innocent unless proven guilty.
1. Convert the transformer Z to 100MVA and 115V bases.
Z115kV,pu=Z13.2kV,pu x (100MVA/21MVA) x (13.2kV/115kV)^2
2. Calculate the short circuit current on the transformer primary side Ip,pu:
Ip,pu=1.0pu/(Zsys,pu+Z115kV,pu)
3. Transfer the short circuit current Ip,pu to the secondary side
Is,pu=Ip,pu x 115kV/13.2kV
4. Express the Ip,pu in Ip,amps
Is,amps=Is,pu x Is,base
where
Is,base=21000kVA/(sqrt3 x 13.2kV)=919A
 
jB,

Not on my monitor screen, they aren't!! Guilty until proven innocent - and this question just can't be from a practising engineer working on substation design because it is such a basic question.

Buy a book and study it like we had to!

-----------------------------------

Start each new day with a smile.

Get it over with.

 
Thanks Jbartos for your feedback and decency. For all the critics, what prompted me to post my thread was to confirm the model I followed, I compared my calc.s with the outcome of trans/dist. analysis software that we use here, the discrepenies were significant, I found the reason was the software uses 'Main' system voltage 'Below' the source as the 'Base' and not the source voltage itself!! I checked with them today and that was their answer!!

There was no need for the harsh words!! anyway, thanks all.

 
lol...guys, all it takes is clicking on the person's username to see what else they have posted...tmaly1 is obviously for real...check out the other posts. Don't be goofy!
 
Sorry mate - I'm usually happy to pitch in and help anyone where I can but from a safety angle I have to say I'm with Scotty on this one as there are many many aspects to consider.

Get professional help (engineering that is).


_______________________________________
Colin J Flatters BSc(Hons) IEng MIEE MIIE
Electrical Engineer / Project Manager
Email - cflatters@colin7.demon.co.uk.
 