Where can I obtain detailed modelling data for fault and dynamic analysis for AC 1MW -5MW generators?

 
Replies continue below

Recommended for you

Manuf should provide. I have some generator dynamics for 5MW mach but no gov.
 
Here are some typical mean values:

Reactances
Type of Gen Subtransient Transient Steady-State
Turbogenerator 10-20% 15-25% 150-230%
Salient-pole gen. 15-25% 25-35% 70-120%

See the enclose document with typical sequence resistance and reactance for small generator


The enclose have some additional information that could be use thread237-27981

Good luck.
 