Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Modification Safety Classification 1

Status
Not open for further replies.

LT1982

Electrical
Jun 17, 2015
4
0
0
US
I have a non-safety related mod and am powering a non-safety related load from a safety-related panelboard class 1E circuit. Does this automatically make my entire mod safety-related?

Thank you
 
Replies continue below

Recommended for you

In my experience, you will have appropriate isolation features between the safety and non-safety portion of your system (e.g., two safety-related fuses). If the modification is occurring entirely "downstream" of your isolation features and does not require changes to the design of the safety portion (I.e., no changes to the characteristics of the load that require your safety-related uninterruptable power system to be modified), then your changes should be non-safety-related.

Your local licensing engineer who is cognizant for Chapter 8 of your FSAR should also be able to help you make the call.
 
While your mod would need to be classified as a Safety Related modification, coincident with the highest safety classification of the components affected by the modification, that doesn't mean that every component added by your modification will need to be classified as safety related. You would need to follow all your procedures and ANSI N45.2.11 requirements for a Safety Related modification and evaluate your impact to the Safety Related components. You also need to make sure you're not violating anything from your original licensing basis, or you may need to go through the 50.59 evaluation process to determine whether you need NRC approval before making the change. Get Licensing involved early in the process.
 
Status
Not open for further replies.
Back
Top