Dear All,

I would like to get your views on the use of modulating non flowing pilot operated PSVs and whether they can mitigate/eliminate the challenges associated with a PSV selected for an orifice size for a governing scenario significantly exceeding other applicable overpressure scenarios.

Considering that oversized PSV would experience a ''cyclic prone chattering'' driven by the high momentum pressure drop at the inlet of the PSV when it momentarily opens at its full bore orifice corresponding rated capacity (above 1/4 of its nozzle area as per API 520). However, do you agree that using a modulated pilot operated PSV (non flowing type) can eliminate/mitigate the issue of oversizing since:
- It will open in response to the required relieving rate needed.
- Non flowing type doesn't mandate fulfilling the 3% inlet pressure loss requirement (as per API 520 PII) and its remote sensing line can sufficiently have an area of 0.07 in2.

Thanks

Regards,
 
Replies continue below

Recommended for you

Pilot PSVs have some advantages compared to direct spring operated PSVs, such as they can typically be a smaller/lighter device for a given capacity and maintaining tight seal.

If the service application doesn't result in plugging of the sensing lines or have issues w/ condensation, pilot reliefs can be a good choice.
 