Modulus of Elasticity of Concrete.

Status
Not open for further replies.

didoT

Geotechnical
Jul 20, 2009
5
I performed some MOE tests on 4"X8" cylinders of high strength concrete (12,000 psi). When i calculate MOE theoretically i get approx. 6,000,000 psi, but the actual test value is approx. 12,000,000 psi. Could this be correct?? I'm following ASTM C469 step by step.
 
Replies continue below

Recommended for you

It is likely that you are measuring the tangent modulus and calculating the secant modulus near the proportional limit, which is ill-defined in concrete.
 
i'm using the equation E= 33 * Wc^1.5 * fc^0.5
Which i don't know if it applies to fc>6000 psi
 