I am relocating a vertical CNC milling machine in my plant and am trying to determine the adequacy of the floor where I plan on placing it.
From old engineering drawings of my plant, the floor is six inches deep concrete reinforced with 6 in. x 6 in. WWF. Talking to my local city engineer (actually the city built this building years ago) he said that most likely there was 4 ft of "silty clay" that was dug out and replaced with 2.5 ft. of "pit run" (sandy gravelly mixture, compacted) and then 18 in. of compacted gravel.
I have an Army/Air Force technical manual that has some design guidelines in it. Based on what I can figure, my application would be considered to be a very heavy stationary live load. Based on that classification, I found a formula that says that
w = 257.876 * s * (square root of (kh/E))
where:
w is the maximum allowable live load (psf)
s is the allowable extreme fiber stress in tension, assumed to be equal to half of the normal 28 day concrete flexural strength, psi
k is the modulus of subgrade reaction, psi
h is the slab thickness, in
E is the modulus of elasticity (4E6 psi)
My problem is this: I do not know what to use for k (modulus of subgrade reaction), neither do I know what to use for s (allowable extreme fiber stress in tension.)
From values listed on a table in the technical manual, k can have values that range from 25 to 300 lb/in^3. Also, the flexural strength for concrete ranges from 550 to 700 psi. (This is where "s" is calculated from.)
I made a spreadsheet that calculated the maximum allowable loads for the entire range of k values and the entire range of flexural strengths. The worst case would be a k value of .25 with the weakest concrete (550 psi). I did this and got a maximum live load of 434 psi. Best case would be a k value of 300 and 700 psi concrete. This gives me a maximum live load of 1915 psi. Obviously quite a difference.
I have two scenarios that I am considering.
1) Placing the machine directly on the floor. The weight of the machine is 26455 lb and outside area of the machine is 92 x 54 inches. This gives me a projected area of 34.5 ft^2, and an average load of 765 psf. However the machine would be on feet and jacks, so there would obviously be higher concentrated loads at certain points.
2) Placing the machine on a steel plate several inches thick to evenly distribute the weight. This plate would be 120 x 150 inches and 3 to 5 inches thick. This would give me a live load of 334 to 436 psf depending on the thickness of the steel plate.
The first option takes me past the max allowable live load at the worst case. The second takes me almost exactly to the limit at worst case.
And finally the question:
Does anyone have a reasonable guess as to what k value I should use? Do these calculations seem reasonable? I have a degree in mechanical engineering and work as a manufacturing engineer/programmer, so I have no background at all in concrete design. I would like an expert in this area to let me know if I am heading in the right direction.
Thanks. One final comment. I only signed up with this site yesterday and listed my field as "mechanical". I would like to target geotechnical engineers with this question, but don't know to do it. I'm not sure how this works. Any ideas?
From old engineering drawings of my plant, the floor is six inches deep concrete reinforced with 6 in. x 6 in. WWF. Talking to my local city engineer (actually the city built this building years ago) he said that most likely there was 4 ft of "silty clay" that was dug out and replaced with 2.5 ft. of "pit run" (sandy gravelly mixture, compacted) and then 18 in. of compacted gravel.
I have an Army/Air Force technical manual that has some design guidelines in it. Based on what I can figure, my application would be considered to be a very heavy stationary live load. Based on that classification, I found a formula that says that
w = 257.876 * s * (square root of (kh/E))
where:
w is the maximum allowable live load (psf)
s is the allowable extreme fiber stress in tension, assumed to be equal to half of the normal 28 day concrete flexural strength, psi
k is the modulus of subgrade reaction, psi
h is the slab thickness, in
E is the modulus of elasticity (4E6 psi)
My problem is this: I do not know what to use for k (modulus of subgrade reaction), neither do I know what to use for s (allowable extreme fiber stress in tension.)
From values listed on a table in the technical manual, k can have values that range from 25 to 300 lb/in^3. Also, the flexural strength for concrete ranges from 550 to 700 psi. (This is where "s" is calculated from.)
I made a spreadsheet that calculated the maximum allowable loads for the entire range of k values and the entire range of flexural strengths. The worst case would be a k value of .25 with the weakest concrete (550 psi). I did this and got a maximum live load of 434 psi. Best case would be a k value of 300 and 700 psi concrete. This gives me a maximum live load of 1915 psi. Obviously quite a difference.
I have two scenarios that I am considering.
1) Placing the machine directly on the floor. The weight of the machine is 26455 lb and outside area of the machine is 92 x 54 inches. This gives me a projected area of 34.5 ft^2, and an average load of 765 psf. However the machine would be on feet and jacks, so there would obviously be higher concentrated loads at certain points.
2) Placing the machine on a steel plate several inches thick to evenly distribute the weight. This plate would be 120 x 150 inches and 3 to 5 inches thick. This would give me a live load of 334 to 436 psf depending on the thickness of the steel plate.
The first option takes me past the max allowable live load at the worst case. The second takes me almost exactly to the limit at worst case.
And finally the question:
Does anyone have a reasonable guess as to what k value I should use? Do these calculations seem reasonable? I have a degree in mechanical engineering and work as a manufacturing engineer/programmer, so I have no background at all in concrete design. I would like an expert in this area to let me know if I am heading in the right direction.
Thanks. One final comment. I only signed up with this site yesterday and listed my field as "mechanical". I would like to target geotechnical engineers with this question, but don't know to do it. I'm not sure how this works. Any ideas?