One of the many reasons why if I see a substitution from G40.20 to A500 it's a no.The workable flat is not the exact as ASTM A500 allows for a greater radius than AISC assumption in the tables. Some that show a workable flat will not have a "flat" with the larger radius vice versa
Yes. I know the fabricator. He is fine with it. The arch. wants to see steel and does not want to see bracing. The aspect ratio of the porch is such that i don't want to cantilever the whole mess of the house.Is the intent here to directly weld the column HSS to the bottom flange of the W10x22? That sounds like a field weld on a screened porch.
I am doing a fixed base as well to get better performance as it is a double story. Moment frame/fixed base to brace the floor system and then more HSS flag poled up to brace the roof.If it's not being too much demand, is there a way to get base fixity and consider the HSS to beam as pinned and still get it to work?
I am showing stiffener plates.Agree with others that fillets should be fine here if it's and R=3 system.
Honestly I think something close to lex's detail would be more stiff than the beam sitting on top of the post (even considering hss sidewall flexibility). Unless you are using some stiffener plates in the beam I would think the flange would flex also.
Yes. The fabricator says he is ok with it. I keep the column flush with the edge of the beam and run a plate up that encompasses the left face of the column and end of the beam web and top flange. The Arch. like the flush look and it seems a bit easier to fabricate.@XR250: wrt to the welding being proposed, would that be done as overhead welding?
I think he's flush only on the end of the beam. So in that case he could weld column>plate>web/flange of beam.If you're flush on the sides then I'd want at least a PJP all around. I only do that type of moment connection with a weld-all-around between the column and the cap plate (beam, in your circumstance as you won't be bolting it).
A part of me winces specifying a 3/16" weld for a moment connection, even if it is good enough in strength.