Monel 400 VS Oxygen

Status
Not open for further replies.

hcjulien

Materials
Aug 14, 2007
47
Hi,

My customer wants to use Monel 400 material for a piping transporting 100% oxygen pressurized inside a pressure piping having walls at 350F.

Do you see any issues? If yes, what are the references (standard, books, etc.) supporting your issues.

Thanks in advance for your help.

hcjulien
 
Replies continue below

Recommended for you

There are a number of standards for this service.
The one that comes to mind is the CGA.
You will need a standard for valves, fittings and other parts.
Maximum flow velocity is also an issue along with temp and pressure.
Monel is a good choice for this service. The old DMIC data from the 60's shows Monel resisting ignition in oxygen at high temperature and pressure.

= = = = = = = = = = = = = = = = = = = =
Plymouth Tube
 
I would suggest you review NFPA 50 and ASME B31.3.
 