Monitoring MV/ LV Ungrounded Systems

Status
Not open for further replies.

Kiribanda

Electrical
May 6, 2003
698
Hi all,

Just a quick question!

Is it a code violation (NEC,National Electrical Safety Code or CEC etc.) to build and opearte a MV or a LV high resistance or an ungrounded elctrical power distribution system without at least a monitoring method or an alarm system to detect and indicate possible phase to ground faults?

If so, can any memebr kindly mention the relevant clause number?

Thanks!

Kiribanda
 
Replies continue below

Recommended for you

NEC Section 250.36 -"High Impedance grounded neutral systems... shall be permitted for 3-phase ac systems of 480 volts to 1000 volts where all of the following conditions are met:
(1) The conditions of maintenance and supervision ensure that only qualified persons service the installation.
(2) Continuity of power is required.
(3) Ground detectors are installed on the system
(4) Line-to-neutral loads are not served."

part (3) requires it.
 