Motor Breaker Sizing...

Status
Not open for further replies.

cfordyce

Electrical
Jun 26, 2002
55
Quick question. Can I put a 40A Breaker on a 20HP rated Inverter driving a 20HP fan motor??? The Inverter is an Allen Bradely 1336 Plus 2 model.

Also, is RWU90 #10 wire OK?
 
Replies continue below

Recommended for you

What voltage?

(#10 AWG cannot be used with a 40A breaker)
 
OK sorry. you're right. #10 is only good for 30 A. I have 32.5 FLA. so I need #8 wire. I will fuse at 30A (TD) and my breaker can be sized up to 60 A according to CE Code. I think I figured it out... I asked question before trying to find answer myself. :)
 
Suggestion:
1. The circuit length is normally given a consideration for allowable voltage drop.
2. 32.5 FLA x 1.25 = 40.625 A. Therefore, the conductor next size is appropriate, e.g. #6AWG @60°C, 55A.
3. Check with the manufacturer for the recommended protection for the drive.
 