For example if I have a 600V motor, should I size consider 575V or 600V?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
[b said:NEC:[/b]
a) The size of the conductors should be at least 125% of the motor FLC [430.22(A)]b) The size the overloads no more than 115% to 125% of the motor nameplate current rating, depending on the conditions [430.32(A)(1)].
c) The short-circuit ground-fault protection device from 150% to 300% of the motor FLC [Table 430.52].]
To accommodate inaccuracy in predicting intermittent system horsepower needs.
To lengthen insulation life by lowering the winding temperature at rated load.
To handle intermittent or occasional overloads.
To allow occasionally for ambient above 40°C.
To compensate for low or unbalanced supply voltages.