Our room air handling units have a 3 speed fan (controlled by a 3 relay output honeywell controller) with a 2uF capacitor.
About a year after installation, we started to suspect "something wrong", and found that most capacitors (measured with a regular multimeter) was around and below 1uF. We found some spare capacitors and started comparison of speed with different (new and old) capacitors. We found that speed was significantly lower (20-40%) with the old capacitors.
Vendor was contacted, and duly sent a team and replaced all capacitors....with some that should be "much better" - these should stay "on top" at least 3 years(!!) Vendor considered capacitors almost a consumable, that they ideally should be replaced every couple of years, but most customers didn't care if they lost a little efficiency and "run them to the fan stopped".
I'm aware many capacitors have a "limited" lifetime, but was not aware that capacitance would drop as quickly as this, and can not find any info indicating they would/should have such a short lifetime in vendors manuals.
For an individual unit I wouldn't care much, but we have more than 1000 units, so we probably need to incorporate "something" to our maintenance schedules....
What is your experience with lifetime on motor capacitors like this?
What is your practice on replacing running capacitors?
By spot check measurement? By time? When unit stops?
About a year after installation, we started to suspect "something wrong", and found that most capacitors (measured with a regular multimeter) was around and below 1uF. We found some spare capacitors and started comparison of speed with different (new and old) capacitors. We found that speed was significantly lower (20-40%) with the old capacitors.
Vendor was contacted, and duly sent a team and replaced all capacitors....with some that should be "much better" - these should stay "on top" at least 3 years(!!) Vendor considered capacitors almost a consumable, that they ideally should be replaced every couple of years, but most customers didn't care if they lost a little efficiency and "run them to the fan stopped".
I'm aware many capacitors have a "limited" lifetime, but was not aware that capacitance would drop as quickly as this, and can not find any info indicating they would/should have such a short lifetime in vendors manuals.
For an individual unit I wouldn't care much, but we have more than 1000 units, so we probably need to incorporate "something" to our maintenance schedules....
What is your experience with lifetime on motor capacitors like this?
What is your practice on replacing running capacitors?
By spot check measurement? By time? When unit stops?