- May 18, 2005
- 150
I just want to consult others on the following. In general for motor protection(typical 3-phase motor) using circuit breakers, reading the NEC, I got:
Branch ckt ground fault & overcurrent protection = not to exceed 250% FLA per Table 430.52
Disconnect device = min 115% - 125% FLA
Branch ckr conductor = 125%
HVAC (motor compressor) = not to exceed 175% HACR-type breakers..(with exception, under certain circumstances shall not exceed 225%)
I realized in reality one needs to confirm with the specific equipment being protected and adjust these protection factors accrodingly, but as a rule of thumb
are these factors typically used? Perhaps there might be different opinions, and I like to hear them. Thanks.
Branch ckt ground fault & overcurrent protection = not to exceed 250% FLA per Table 430.52
Disconnect device = min 115% - 125% FLA
Branch ckr conductor = 125%
HVAC (motor compressor) = not to exceed 175% HACR-type breakers..(with exception, under certain circumstances shall not exceed 225%)
I realized in reality one needs to confirm with the specific equipment being protected and adjust these protection factors accrodingly, but as a rule of thumb
are these factors typically used? Perhaps there might be different opinions, and I like to hear them. Thanks.