CircuitSolver
Electrical
- May 7, 2007
- 4
Is it common practice to use current limiters with circuit breakers to limit short circuit current in power circuits for smaller loads fed from Motor Control Centers (MCCs)? I am finding that when sizing cables for available short-circuit currents per ICEA P-32-382-2007 that I have to upsize cables frequently for smaller loads like Motor Operated Valves (MOVs) and smaller pumps. I understand that ICEA P-32-382-2007 is generally conservative to account for faults at any point in a circuit, and this leads to the results that I am getting. Is there any additional guidance that would allow me to justify a smaller cable size for this application?