We recently had a coupler fail on a prelube pump for a 5 stage turbine air compressor. That style of coupler has been replaced with a lovejoy coupler.
This pump is driven by a 1750 r/m 3ph. 5 HP 480V motor. No load, the motor draws 2.5 A/ phase. Loaded as it is now, it draws 4.2A/4.4A/4.5A for each phase respectively. Nameplate states 6.2 Amps and the overload is set for 7 amps. While the alignment of the motor is not PERFECT (off horizontally maybe a mm) vibration is minimal. Actually, it seems very smooth. I don't feel current draw is too much either. My question is: Does anybody see a problem with this?
Oh, while I do not know the GPM of the pump, the main oil lines are 2 inch and the pressure is 28-30psi.
Thanks in advance,
Scott
I really am a good egg, I'm just a little scrambled!
We recently had a coupler fail on a prelube pump for a 5 stage turbine air compressor. That style of coupler has been replaced with a lovejoy coupler.
This pump is driven by a 1750 r/m 3ph. 5 HP 480V motor. No load, the motor draws 2.5 A/ phase. Loaded as it is now, it draws 4.2A/4.4A/4.5A for each phase respectively. Nameplate states 6.2 Amps and the overload is set for 7 amps. While the alignment of the motor is not PERFECT (off horizontally maybe a mm) vibration is minimal. Actually, it seems very smooth. I don't feel current draw is too much either. My question is: Does anybody see a problem with this?
Oh, while I do not know the GPM of the pump, the main oil lines are 2 inch and the pressure is 28-30psi.