Good morning!
I have 220V to a motor wired Delta, it's rated current is 13.2A. The draw is 16A and tripping overload.
Megger readings are good, resistance shows slight difference between windings, however inductance reading
on two windings is 9.3mh the third is 9mh.
Would .3mh indicate a shorted winding and would such small a value cause that much more current? What is the
formula for calculating this difference?
Thank's