batman2010
Electrical
- May 28, 2010
- 31
Hi all,
when specifying a motor disconnect switch according to art.(430.110) of NEC it shall not be less than 115% of the FLA of the motor; sticking with this formula will lead to a disconnect rating less than the rating of the circuit breaker protecting the motor which means the inrush starting current of the motor will be more than the rating of the disconnect switch; I always wondered doesn't this affect the disconnect switch after a period of time? isn't better to specify a disconnect switch with the same rating or more than the circuit breaker?
your inputs are appreciated.
Thank you
when specifying a motor disconnect switch according to art.(430.110) of NEC it shall not be less than 115% of the FLA of the motor; sticking with this formula will lead to a disconnect rating less than the rating of the circuit breaker protecting the motor which means the inrush starting current of the motor will be more than the rating of the disconnect switch; I always wondered doesn't this affect the disconnect switch after a period of time? isn't better to specify a disconnect switch with the same rating or more than the circuit breaker?
your inputs are appreciated.
Thank you