Motor Full Load Current

Status
Not open for further replies.

Timm1

Electrical
Apr 13, 2009
12
The table of full load amperes in NEC states that the current values shall be multiplied by 1.1 and 1.25 for power factors of 0.9 and 0.8 respectively. But in actual practice, we don’t multiply by these factors for the calculations of the motor feeder conductor. I understand that all real motors have a power factor between 0.8-0.9. So I am wondering why we don’t use these factors in practice?
 
Replies continue below

Recommended for you

You're talking about 430.250. That note at the bottom applies to the currents given for synchronous machines at unit power factor. It does not apply to the currents given for induction motors.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 