Hello
I have a bit of a strange problem
In work we are running a 1MW MG set which starts OK with no problem, from 1 of 2, 1.5MW Diesel Generators
However a test we have to complete, is to trip the MG and then restart it during its run-down period
on a number of occasions within an hour
This has been dome before on other units with no problem
For some reason we get a number of trips of Phase Inbalance when we try and do this while the MG is running down
The Supply Breaker which feeds the DG with the power opens and says Phase Inbalance on the Reverse Power protection Unit
This happens on either DG
As it runs fine from a stopped position, it is hard to understand why starting with momentum should cause a problem but it does
The insulation may be dropping as it heats up, from over 100MOhm to maybe 2 MOhms
It doesn't trip every time
Any advice welcome, as its all a bit strange
I have a bit of a strange problem
In work we are running a 1MW MG set which starts OK with no problem, from 1 of 2, 1.5MW Diesel Generators
However a test we have to complete, is to trip the MG and then restart it during its run-down period
on a number of occasions within an hour
This has been dome before on other units with no problem
For some reason we get a number of trips of Phase Inbalance when we try and do this while the MG is running down
The Supply Breaker which feeds the DG with the power opens and says Phase Inbalance on the Reverse Power protection Unit
This happens on either DG
As it runs fine from a stopped position, it is hard to understand why starting with momentum should cause a problem but it does
The insulation may be dropping as it heats up, from over 100MOhm to maybe 2 MOhms
It doesn't trip every time
Any advice welcome, as its all a bit strange