We operate a 3500 foot long inclined belt conveyor. The conveyor is powered by two 2500 HP induction motors, and the motors are coupled to the drive through fixed fill fluid couplers. For some reason, during a "routine" stop, the rollbacks failed to engage and the loaded conveyor rolled backwards, overspeeding the drive system (in reverse) and causing considerable mechanical damage. The fluid couplers failed catastrophically due to high speed operation. Fortunately no one was injured.
Each motor is protected by a MultLin overload relay which operates a non-reversing vacuum linestarter. Power factor correction capacitors are installed on the load side of the linestarter and switched with the motor. The maximum allowable KVAC is 592 KVAC per motor, and the installed KVAC is 400 KVAC per motor. The CT providing information to the Multilin is installed between the motor and capacitor. Both vacuum linestarters are fed from a common 4160 volt bus.
When data was extracted from the Multilin, about 30 seconds after the "routine" stop, there was a "blip" of current detected by the CTs - one motor shows a negative KW and KVAR reading possibly indicating that the motor was acting as a generator feeding power into the capacitor bank. The other motor showing KW and KVAR readings of the same approximate magnitude, but in the positive direction. It may be academic at this point, but can I assume that both motors were acting as generators during this episode?
Typical motor start information:
I = 1500 Amps
V = 3500 Volts
KW = 2200
KVAR = 9000.
During this episode:
I = 30 Amps (approx.)
V = 4060 Volts
KW = -25 (+30 in other motor)
KVAR = -220 (+230 in other motor)
I am interested in your thoughts,
Regards,
Raisinbran
Each motor is protected by a MultLin overload relay which operates a non-reversing vacuum linestarter. Power factor correction capacitors are installed on the load side of the linestarter and switched with the motor. The maximum allowable KVAC is 592 KVAC per motor, and the installed KVAC is 400 KVAC per motor. The CT providing information to the Multilin is installed between the motor and capacitor. Both vacuum linestarters are fed from a common 4160 volt bus.
When data was extracted from the Multilin, about 30 seconds after the "routine" stop, there was a "blip" of current detected by the CTs - one motor shows a negative KW and KVAR reading possibly indicating that the motor was acting as a generator feeding power into the capacitor bank. The other motor showing KW and KVAR readings of the same approximate magnitude, but in the positive direction. It may be academic at this point, but can I assume that both motors were acting as generators during this episode?
Typical motor start information:
I = 1500 Amps
V = 3500 Volts
KW = 2200
KVAR = 9000.
During this episode:
I = 30 Amps (approx.)
V = 4060 Volts
KW = -25 (+30 in other motor)
KVAR = -220 (+230 in other motor)
I am interested in your thoughts,
Regards,
Raisinbran