Dear All,
Please, I need some advice,
I have a problem with my motor. The motor with 380 V, 3 phase, 50 Hz, 2 pole, 150kW suddenly shutdown after running around 2 hours. The 50G relay (groundfault relay) was actived. I measured insulation resistance by 500VDC and winding resistance , result :
R phase 2.55 Mohm/ 0.0135 ohm
S phase 2.50 Mohm/ 0.0136 ohm
T phase 2.60 Mohm/ 0.0135 ohm
Based on this, I started motor again until 4 hours and I measured current (ampere) and voltage each phase were normal and vibration was normal ( there was nothing electrical problem ). Vibration at 2H (maximum value) overall below 1.5 mm/s RMS. I take with Fmax 200 Hz and resolution 6400 lines.
I stopped motor and I measured insulation resistance was increased each phase around 50 Mohm. I conducted heating up the motor until insulation resistance reach 150 Mohm.
After 3 days, I checked insulation resistance and I got insulation resistance were decrease (each phase) become 3.50 Mohm
Would you like to explain me:
What is problem with my motor?
Why insulation resistance decrease in 3 days?
Please, give me some advice for this condition.
Regards,
pjono
Please, I need some advice,
I have a problem with my motor. The motor with 380 V, 3 phase, 50 Hz, 2 pole, 150kW suddenly shutdown after running around 2 hours. The 50G relay (groundfault relay) was actived. I measured insulation resistance by 500VDC and winding resistance , result :
R phase 2.55 Mohm/ 0.0135 ohm
S phase 2.50 Mohm/ 0.0136 ohm
T phase 2.60 Mohm/ 0.0135 ohm
Based on this, I started motor again until 4 hours and I measured current (ampere) and voltage each phase were normal and vibration was normal ( there was nothing electrical problem ). Vibration at 2H (maximum value) overall below 1.5 mm/s RMS. I take with Fmax 200 Hz and resolution 6400 lines.
I stopped motor and I measured insulation resistance was increased each phase around 50 Mohm. I conducted heating up the motor until insulation resistance reach 150 Mohm.
After 3 days, I checked insulation resistance and I got insulation resistance were decrease (each phase) become 3.50 Mohm
Would you like to explain me:
What is problem with my motor?
Why insulation resistance decrease in 3 days?
Please, give me some advice for this condition.
Regards,
pjono