NCTHAI
Electrical
- Nov 26, 2007
- 98
We are commissioning the plant and carrying out no load run 3 similar 6KV / 1000 KW / 8 poles / 118A / motors. For 2 motors we have seen the motor KW of 28KW but for one of the motor motor KW of 13 KW. The no load current of motor per data sheet is 42A at 6000KV. We have seen 46 A for all three motors at 6400 V.
Attached are the motor current and voltage waveform captured through relay and plotted in excel file. As seen for good motor, current and voltage phase sequence is RYB. But for bad motor, voltage phase sequence is RYB and current phase sequence is RBY.
What can be the issue here? - incorrect Current transformer phase sequence? or phase sequence is correct but there is polarity for C phase is reversed? Did not see any temperature rise in relay or through RTD measurement during the 2 hours run.
Please share your thoughts.
Attached are the motor current and voltage waveform captured through relay and plotted in excel file. As seen for good motor, current and voltage phase sequence is RYB. But for bad motor, voltage phase sequence is RYB and current phase sequence is RBY.
What can be the issue here? - incorrect Current transformer phase sequence? or phase sequence is correct but there is polarity for C phase is reversed? Did not see any temperature rise in relay or through RTD measurement during the 2 hours run.
Please share your thoughts.