Motor torque performance (especially during transients such as acceleration) is carefully chosen against the required load torque for the process. There are multiple ways to change the shape of the motor's torque curve to better suit a specific load profile: the methods range from choosing a different material conductivity (i.e. rotor bar and/or ring) to modifying internal geometry (slot size/count, location and number of air ducts, radial air gap, etc.) to simply increasing the machine's steady-state power output (so that the per unit values for transient performance are based on a larger "base" number).
From the OP's description, it sounds like the "default" SKM design is a NEMA B, where the specific fan application (for whatever reason) needs something a bit more like a D.
The first step is to verify the actual fan load torque (curve) requirements. The second is to verify the motor torque performance.
When modeling your 44kW motor in SKM, ensure that the motor's torque characteristics align with your fan load requirements. Discrepancies may arise from using generic library data. For precise modeling, consider sourcing detailed motor specifications from reliable suppliers like
Ovaga Technologies. Their expertise in electronic components can provide the accurate data needed to enhance your simulation's fidelity.