Jeff_Cameron
Electrical
- Mar 6, 2020
- 2
Hi all,
I am having an issue with some motors on a piece of industrial machinery. The problem I am having is that the motor overloads keep tripping for all of my coolant supply pumps. This is really a 2 part question.
Part 1: I have a 480v 3 phase motor with a nameplate FLA of 28.0A (at 480v). the overload is tripping up to 12 times a day. Full disclosure, I did not design THIS system. the motor overload is a Siemens overload with a max rating of 32A. I did notice that although the overload is rated up to 32A, the max horsepower rating for the overload is 20HP. The motor is rated at 25HP. The ambient air inside the panel is approx. 98 degrees F. The ambient air outside of the panel is 73-75 degrees F. Thermal imaging of the panel shows that the overload is reaching temps of up to 150 degrees F. The wires going to the overloads are around the same and the cables on the outside of the machine running to the motors are also significantly warm. the motors have cycle time of about 1.5 hours, during which there are valves opening and closing periodically. The motors are definitely not short-cycling. all wire terminations have been checked for sufficient tightness. Does anyone have any idea why this could be happening? is it just as simple as the overloads need to be sized for a higher HP to account for the heat? Also, the service factor is the standard 1.15.
Part 2: In general I understand that an electrical horsepower is equivalent to roughly 746 watts. How does the horsepower figure into the amperage sizing of a motor? for instance, this motor is 25 HP. If i take 25 x 746, i get 18,650w. i then divide that by 480 and get 38.85A. Do i then need to divide that by 1.732? doing so gives me 22.43A. even with that, where do they get 28 from? is that just because that's the full load condition? Its been a long time since I went to school for this so I may have forgotten a few things. thank you for your help I sincerely appreciate it.
I am having an issue with some motors on a piece of industrial machinery. The problem I am having is that the motor overloads keep tripping for all of my coolant supply pumps. This is really a 2 part question.
Part 1: I have a 480v 3 phase motor with a nameplate FLA of 28.0A (at 480v). the overload is tripping up to 12 times a day. Full disclosure, I did not design THIS system. the motor overload is a Siemens overload with a max rating of 32A. I did notice that although the overload is rated up to 32A, the max horsepower rating for the overload is 20HP. The motor is rated at 25HP. The ambient air inside the panel is approx. 98 degrees F. The ambient air outside of the panel is 73-75 degrees F. Thermal imaging of the panel shows that the overload is reaching temps of up to 150 degrees F. The wires going to the overloads are around the same and the cables on the outside of the machine running to the motors are also significantly warm. the motors have cycle time of about 1.5 hours, during which there are valves opening and closing periodically. The motors are definitely not short-cycling. all wire terminations have been checked for sufficient tightness. Does anyone have any idea why this could be happening? is it just as simple as the overloads need to be sized for a higher HP to account for the heat? Also, the service factor is the standard 1.15.
Part 2: In general I understand that an electrical horsepower is equivalent to roughly 746 watts. How does the horsepower figure into the amperage sizing of a motor? for instance, this motor is 25 HP. If i take 25 x 746, i get 18,650w. i then divide that by 480 and get 38.85A. Do i then need to divide that by 1.732? doing so gives me 22.43A. even with that, where do they get 28 from? is that just because that's the full load condition? Its been a long time since I went to school for this so I may have forgotten a few things. thank you for your help I sincerely appreciate it.