motor overloads standards 2

Status
Not open for further replies.

ilian

Electrical
Sep 25, 2001
1
I am looking for any standardized information on overloads motors should withstand relatively to their power rating.
Is there any norm or admitted standard about that ?

Thank you
 
Replies continue below

Recommended for you

NEMA MG-1 only required rated temperature rise at rated load (or service factor rise at service factor load). That doesn't tell us anything about overload capability... except if it has a service factor... in which case the rise at service factor load is approx 10C above the normal required rise at rated load... equating roughly to a halving of insulation life. But there is a lot more that can be said about service factor... search this forum.

The fact that NEMA also allows the standard motor to operate at a voltage up to 10% low would seem to imply to me that NEMA is suggesting motors contain at least 10% overload capability.

Motor overload protective settings for 49 device are typically in the range of 115%-125%FLA and higher for service-factor rated motors. Some info in IEEEC37.96 section 7.2.9.1. I'm not sure exactly where these numbers originated, it may be the NEC.

The motor purchaser can request from the manufacturer a thermal damage curve IAW IEEE620-1996 which will define exactly how much time is allowed for any given level of overload. Alternatively if the motor is required to have a known short-time duty above rated, the user can make this part of his specification.





 
I agree with electricpete and would only add that you should not expect any overload capability beyond what is provided by the motor's service factor and duty specifications.



 
Electricpete is on the money as always:)

I would also like to add that the report from GAMBICA for vfd's is really good as far as insulation stresses for motors including NEMA MG1 pt 31 and IEC 60034-17 (the other motor standard that I see more and more these days.)