Motor Protection 51 Settings

Status
Not open for further replies.
Replies continue below

Recommended for you

Use inverse time overcurrent for overload protection and an instantaneous overcurrent for short circuit protection. Set the curve to match the motor overload curve. Usually set pickup at 115%-125% of Full Load Amps (FLA) with the time dial adjusted to trip on Locked Rotor Current faster than the allowable hot stall time and slower than the motor/load's acceleration time.

Set instantaneous above the motor inrush current.

You will need the motor thermal limit curves to properly set the relay.
 