Actually, it depends on what else is in the protection scheme. Bill hit it on the nose in terms of why it was outlawed, but even here in North America we allow an exception to that rule if there are " other means of protection". So for example if you have thermistor or RTD thermal sensors, they will provide the missing thermal protection necessary when using only 2 sensors. the issue is, current imbalance will heat a motor disproportionately to the amount of current flow, so current monitoring becomes a less effective means of motor protection in that case, and having only 2 sensors makes complete imbalance protection very difficult. So adding back in some other form of thermal protection, especially something more direct such as RTDs or even Thermistors, is a way of compensating for that shortcoming.
What often happens however is that people ASSume that the thermal device system is optional, don't use it, and lose the motor, then wonder why. So to that end, it is better to start out with a 3 CT solution, then add the thermal devices if you feel it is necessary. That's what most of us do.
By the way, 6kV motors are typically on something VERY important in a plant. Deciding on using the cheapest junk motor protector available (as evidenced by having only 2 CTs) can end up being the most costly decision they have made.