Motor Rated BP 3

Status
Not open for further replies.

jjgas

Petroleum
Apr 4, 2006
1
Help! I am a Gas Engineer and am reading a document with spec for electric motor. One section states "....unless the full load BP is less than or equal to 85% of the motor rated BP". Q. Is BP referring to Byass? If not, what?

Grateful for nay help. jjgas
 
Replies continue below

Recommended for you

It would make sense if "BP" was actually "bhp" for brake horsepower. This is the power required by the driven equipment at the shaft.

A common motor sizing spec is to require the motor nameplate horsepower to be equal to the driven equipment's maximum bhp IF the motor has a Service Factor of 1.15. If the motor has a Service Factor of 1.00, the driven equipment bhp cannot exceed 85% (or 87%) of the motor nameplate hp.

 
It seems to be "braking power" , the mechanical power applied by the load to the motor shaft as for stopping it. In America we use BHP for the power measured in Horsepower.
 
Could be either really, depending on the context. Can you give us more details?