Motor rated voltage

Status
Not open for further replies.

Lc85

Electrical
Apr 14, 2011
107
Our motor supplier has offered an IEC motor with a rated voltage 380-400-415V(Multivoltage). The supply voltage from the client is 400V +/- 10% so potentially the motor could see 360V & 440V. My question is would this motor be able to cope with these fluctuations? I know that there is a 10% tolerance on IEC motors but how does that work for multiple voltage?

Thanks very much
 
Replies continue below

Recommended for you

Should be fine. Watch for limitations on the ATEX certificate if this is a hazardous area motor - some don't allow large variance in the supply voltage.
 
I would connect the motor for 400V to give you the 10% in each direction. If you go with 380V, it may go above 10% on the high end. If you go with 415V, it may go below 10% on the low end.

I am an engineer, so the glass is twice as big as it needs to be.
 
I'd be surprised if there are multiple tappings instead of the standard six posts.
 