Now this:
A compressor motor was installed in 1972. A 1600 kW 3 kV asynchronous motor. It is fed from its own transformer, 20/3 kV 2 MVA and 7 percent uk.
The motors have always been equipped with Pt100 temperature transducers but these have been connected to a not-so-reliable temperature indicator and no-one really cared what they said. The temperatures seemed to be in the 90 - 95 centigrades region most of the time.
Now, the indicator system has been replaced with a new one and everything has been checked out. The temperature is now rising to 140 C within one hour and still increasing. The isolation class is B (yes, old machine) so the people closed the machine down and yelled for help.
Checked cooling, heat exchanger, motor voltage, symmetry, distortion, slip, current consumption - I think everything. All OK.
The conclusion is that the motor probably has been running quite hot before the change of temperature indicators - but no-one knew. My question: Is it at all possible to run a class B motor for years at temperatures close to or slightly above 150 C?
(Yes, I know about the halfing for each 8 - 10 C increase in temperature. It is not that part of the problem I am trying to grasp. The question is more like this: are there any "magic limits" that makes a vintage class B insulation break down very quickly or do we still follow the "2exp(-T/10)" law?
In other words: Is it probable that the motor has been running 20 - 30 C above rated temperature for many years?
A compressor motor was installed in 1972. A 1600 kW 3 kV asynchronous motor. It is fed from its own transformer, 20/3 kV 2 MVA and 7 percent uk.
The motors have always been equipped with Pt100 temperature transducers but these have been connected to a not-so-reliable temperature indicator and no-one really cared what they said. The temperatures seemed to be in the 90 - 95 centigrades region most of the time.
Now, the indicator system has been replaced with a new one and everything has been checked out. The temperature is now rising to 140 C within one hour and still increasing. The isolation class is B (yes, old machine) so the people closed the machine down and yelled for help.
Checked cooling, heat exchanger, motor voltage, symmetry, distortion, slip, current consumption - I think everything. All OK.
The conclusion is that the motor probably has been running quite hot before the change of temperature indicators - but no-one knew. My question: Is it at all possible to run a class B motor for years at temperatures close to or slightly above 150 C?
(Yes, I know about the halfing for each 8 - 10 C increase in temperature. It is not that part of the problem I am trying to grasp. The question is more like this: are there any "magic limits" that makes a vintage class B insulation break down very quickly or do we still follow the "2exp(-T/10)" law?
In other words: Is it probable that the motor has been running 20 - 30 C above rated temperature for many years?