collies99
Electrical
- May 28, 2010
- 198
Motor Data: 3500 HP SCIM, 95% efficiency, 4160V, Xd" = .18 or 1.133 ohm on 6.29 ohm base. Full voltage start cct.
CT Data: I have three zero seq CTs at the motor in standard differential config; T1-T4, T2-T5, T3-T6. It is a C50, ratio 100:5A.
My CT loop resistance measured at 2.3 ohms and CT sec winding resistance at .5 ohms.
I have doubt that the differential protection will work for high magnitude internal motor fault current. CT will saturate and unable to detect phase-to-phase faults in the group jumps or in the stator slots. I have a GE Multilin M60 which have filter and respond to fundamental frequency only. Low level faults I have no issues, just high magnitude phase-to-phase faultsfault even terminal faults downstream of the CTs.
CT Data: I have three zero seq CTs at the motor in standard differential config; T1-T4, T2-T5, T3-T6. It is a C50, ratio 100:5A.
My CT loop resistance measured at 2.3 ohms and CT sec winding resistance at .5 ohms.
I have doubt that the differential protection will work for high magnitude internal motor fault current. CT will saturate and unable to detect phase-to-phase faults in the group jumps or in the stator slots. I have a GE Multilin M60 which have filter and respond to fundamental frequency only. Low level faults I have no issues, just high magnitude phase-to-phase faultsfault even terminal faults downstream of the CTs.