Hello,
I am using a softstarter for a 6.6kV, 1650kW motor (FLA=172A,LRA=5x172A) by limiting the current to 250% for 14 seconds where as the motor max. stalling time is 20sec at 100% term. voltage.
Although the current is limited to 250% for the 14secs, it reaches a peak of ~340% soon after the 14secs and this is causing a significant voltage drop in the system.
My understanding is that current limiting indirectly limits the voltage on the motor terminals and doesn't allow the motor to reach full voltage. After 14secs, the voltage on the motor terminal shall reach the line voltage and the motor reaches rated conditions.
Can anyone share your knowledge on this kind of scenarios?. I want to avoid starting current more than the set 250%.
Attached the plot from etap
Thank you
I am using a softstarter for a 6.6kV, 1650kW motor (FLA=172A,LRA=5x172A) by limiting the current to 250% for 14 seconds where as the motor max. stalling time is 20sec at 100% term. voltage.
Although the current is limited to 250% for the 14secs, it reaches a peak of ~340% soon after the 14secs and this is causing a significant voltage drop in the system.
My understanding is that current limiting indirectly limits the voltage on the motor terminals and doesn't allow the motor to reach full voltage. After 14secs, the voltage on the motor terminal shall reach the line voltage and the motor reaches rated conditions.
Can anyone share your knowledge on this kind of scenarios?. I want to avoid starting current more than the set 250%.
Attached the plot from etap
Thank you