Had an interesting one here at the plant this morning. We had a size 5 starter bucket develop a serious arc flash of some sort. After electricians were told that a motor tripped they went to the MCC and noticed that the starter bucket door was blown open and the entire MCC bucket and starter was covered in black soot, and several wires inside the bucket were melted.
The starter like I mentioned is a size 5 starter with a 200hp 480V motor connected to it. The instantaneous motor circuit breaker on the line side of the starter was a 400A circuit breaker which did not trip.
Its hard to tell where the fault occured because the arc flash caused several things to melt. From what I can tell it may have occured on one of the wires that connects the busbar stabs to the line side of the breaker. These wires are melted and broken and both the stabs and the bus bar show corrosion markings.
The thing that puzzles me is why the breaker upstream of the MCC did not trip. The MCC is a 480V 2000A bus MCC which is serviced by a 4.16D-480VY 1500kVA transformer. On the secondary of the transformer there is a 480V 2000A Siemens RL breaker with a Static II trip unit. I am thinking this breaker should have tripped before this starter blew apart???
For this starter to blow apart I am thinking there had to be some serious fault current present. The instantaneous setting on the RL breaker is set for 24,000A and the ground fault setting is set for 1200A for .25s. Should this breaker should have tripped before we damaged this starter and MCC?