vosstire
Automotive
- Jul 5, 2006
- 2
I have a US Motor model N865 30hp three phase motor, 208/230/460 on 208 service. This motor drives a Webtrol pump which cycles about 100 times per hour and provides rinse water at about 600psi. The motor starter is a Moeller DIL4M115 (24V50/60HZ) part number 209758 and is rated at 40hp.
We have fused three starters through about 100 cycles. I had an independent electrical testing agency inspect and test all components to confirm proper installation. No problems were identified. We have check the incoming power from the power company and the service voltage is closely around 208. The power company has put a recorder on the 150KV transformer which supplies us to check the output. I am awaiting results. Our total requirements for the site are about 750 amps, with the 30hp motor being the largest. We have five 10hp blowers that also cycle about the same and miscellaneous 2-5 hp motors servicing other equipment. Still the starter fails.
I have an identical installation using a Benshaw NEMA rated starter (same motor, same service) and have had no problems for the past year.
Is there such a difference between a Moeller Starter (IEC) than a Benshaw (NEMA) starter???
We have fused three starters through about 100 cycles. I had an independent electrical testing agency inspect and test all components to confirm proper installation. No problems were identified. We have check the incoming power from the power company and the service voltage is closely around 208. The power company has put a recorder on the 150KV transformer which supplies us to check the output. I am awaiting results. Our total requirements for the site are about 750 amps, with the 30hp motor being the largest. We have five 10hp blowers that also cycle about the same and miscellaneous 2-5 hp motors servicing other equipment. Still the starter fails.
I have an identical installation using a Benshaw NEMA rated starter (same motor, same service) and have had no problems for the past year.
Is there such a difference between a Moeller Starter (IEC) than a Benshaw (NEMA) starter???