Marke
Electrical
- Oct 20, 2001
- 1,212
Those of us in the 50 Hz world have seen a change in motor designs in recent years, particularly the rotor design with a push for higher efficiency motors. The high efficiency is often achieved by the use of lower impedance rotor bars which results in lower slip losses. The down side of this has been that the high slip operating conditions have been severely compromised. This shows up as an increase in the Locked Rotor Current of the motor.
I have just completed a design project whereby two pumps are to be run of a diesel generator set. One pump is 75KW and the other is 37KW. The 75KW pump always will be started first. In order to optimize the generator set sizing, I went on the hunt for a 75KW 2 pole motor that had a high "starting efficiency". To my dismay, I found that although years ago, it was possible to find motors that would enable me to start this pump at around 300% start current, the modern motors needed start currents of around 400 - 450% The best I found was 350%. I do not know if there has been a similar trend in the Nema range of motors.
To me, this may have been a gain in the full speed running efficiency of motors, but it is a definite backward step when it comes to starting the motors. On weak supplies and standby generators, the starting current is very important. Pump stations with only one pump running from a dedicated generator have to have an engine sized for the start conditions. This results in an oversized engine which runs lightly loaded and quickly suffers glazed bores.
Perhaps as engineers, we need to bring some pressure to bear to ensure that the starting characteristics of induction motors are taken seriously by the regulatory bodies as well as the running efficiency.
I am interested in the comments and experiences of others.
Best regards,
Mark Empson
I have just completed a design project whereby two pumps are to be run of a diesel generator set. One pump is 75KW and the other is 37KW. The 75KW pump always will be started first. In order to optimize the generator set sizing, I went on the hunt for a 75KW 2 pole motor that had a high "starting efficiency". To my dismay, I found that although years ago, it was possible to find motors that would enable me to start this pump at around 300% start current, the modern motors needed start currents of around 400 - 450% The best I found was 350%. I do not know if there has been a similar trend in the Nema range of motors.
To me, this may have been a gain in the full speed running efficiency of motors, but it is a definite backward step when it comes to starting the motors. On weak supplies and standby generators, the starting current is very important. Pump stations with only one pump running from a dedicated generator have to have an engine sized for the start conditions. This results in an oversized engine which runs lightly loaded and quickly suffers glazed bores.
Perhaps as engineers, we need to bring some pressure to bear to ensure that the starting characteristics of induction motors are taken seriously by the regulatory bodies as well as the running efficiency.
I am interested in the comments and experiences of others.
Best regards,
Mark Empson