noel0589
Electrical
- Sep 23, 2004
- 50
Hi all,
I saw the subject on contactors come up again.
Please download the above.
Page 3 of attachment (hb.pdf) shows wye delta starting of a 40HP/200V motor using 208V/60Hz/3Phase power supply.
Scale is 250A / div. (A) and 50ms/div (horizontal) Page 3 shows no problem during start.
Now please look at page 2
In this case, heavy arcing occurred. On delta connection the graph on page 2 shows how the current was interrupted during 2 cycles. I am not sure to attribute this to bouncing of the contactor or to a voltage drop in the power supply affecting the contactor magnetic coils capacity to hold.
Page 1 shows line to line voltage (V is 300V peak) and current under heavy arcing condition.
My thinking is that the surge of current(transient current) results in a large voltage drop in the voltage supply line. This drop in voltage results in contactor coil magnetic field weakening and causes delta contacts to break at high current causing the large arc. When delta is disconnected, supply voltage recovers and contactor closes once again.
Can you provide me with advice on my reasoning?
My main question is the time scale. Can all of the above happen within such a short time span of 2 cycles?
Thank you!!
I saw the subject on contactors come up again.
Please download the above.
Page 3 of attachment (hb.pdf) shows wye delta starting of a 40HP/200V motor using 208V/60Hz/3Phase power supply.
Scale is 250A / div. (A) and 50ms/div (horizontal) Page 3 shows no problem during start.
Now please look at page 2
In this case, heavy arcing occurred. On delta connection the graph on page 2 shows how the current was interrupted during 2 cycles. I am not sure to attribute this to bouncing of the contactor or to a voltage drop in the power supply affecting the contactor magnetic coils capacity to hold.
Page 1 shows line to line voltage (V is 300V peak) and current under heavy arcing condition.
My thinking is that the surge of current(transient current) results in a large voltage drop in the voltage supply line. This drop in voltage results in contactor coil magnetic field weakening and causes delta contacts to break at high current causing the large arc. When delta is disconnected, supply voltage recovers and contactor closes once again.
Can you provide me with advice on my reasoning?
My main question is the time scale. Can all of the above happen within such a short time span of 2 cycles?
Thank you!!