At the following link are powerpoint slideshows of starting current waveforms during two starts of a 2500hp motor.
There are unusual simultaneous subcycle-duration bursts of current on all three phases prior to each start, as if perhaps all three breaker contacts were bouncing together several times prior to finally closing. Once finally closed the current waveforms are as expected with decaying dc offset. But if that is what is going on I am at a loss to explain how the current attains such a high magnitude in such a short period of time.
The system is 13.2kv low-resistance grounded system (20-ohm transformer secondary neutral grounding resistor). The motor is connected ungrounded wye and has gronded-wye surge capacitors attached to the terminals.
I have phase-to-phase voltage traces from the bus which show no anomalies (phase to ground not available).
My primary interest is to try to understand how these current waveforms discussed can occur.
I know some strange things can happen when switching capacitors but I really can't quite picture what can be going on here.
FYI - Here is overview of why we are monitoring the current during starting of this motor:
We experienced 3 trips of a 2500hp 13.2kv motor upon starting over a 2 year period.
It is not reproducible. It did not recur during the monitored starts.
This is some confusion on which protective flags were actually received.
Relays tested OK. Motor and cable meggered ok. Motor ok by partial discharge test.
CT excitation and ratio tests sat. ct/relay circuit meggered to ground sat with ct neutral ground lifted.
CT ratio is 40:1. All quantities in secondary amps.
Normal Running current (less than full load) ~ 1.8A
Full load amps ~ 2.5A
Locked Rotor Current =15A
Hi Dropout Trip setpoint 20A (if does not dropout within 0.1 sec).
Instantaneous setpoint 24A
During these two monitored starts the motor did not trip. However the peak of the bursts of current do exceed the peak value of the instantaneous setpoint (35*1.41), although apparently not long enough to cause a trip in this case. Also it seems plausible we may have been close to tripping the high dropout.
There are unusual simultaneous subcycle-duration bursts of current on all three phases prior to each start, as if perhaps all three breaker contacts were bouncing together several times prior to finally closing. Once finally closed the current waveforms are as expected with decaying dc offset. But if that is what is going on I am at a loss to explain how the current attains such a high magnitude in such a short period of time.
The system is 13.2kv low-resistance grounded system (20-ohm transformer secondary neutral grounding resistor). The motor is connected ungrounded wye and has gronded-wye surge capacitors attached to the terminals.
I have phase-to-phase voltage traces from the bus which show no anomalies (phase to ground not available).
My primary interest is to try to understand how these current waveforms discussed can occur.
I know some strange things can happen when switching capacitors but I really can't quite picture what can be going on here.
FYI - Here is overview of why we are monitoring the current during starting of this motor:
We experienced 3 trips of a 2500hp 13.2kv motor upon starting over a 2 year period.
It is not reproducible. It did not recur during the monitored starts.
This is some confusion on which protective flags were actually received.
Relays tested OK. Motor and cable meggered ok. Motor ok by partial discharge test.
CT excitation and ratio tests sat. ct/relay circuit meggered to ground sat with ct neutral ground lifted.
CT ratio is 40:1. All quantities in secondary amps.
Normal Running current (less than full load) ~ 1.8A
Full load amps ~ 2.5A
Locked Rotor Current =15A
Hi Dropout Trip setpoint 20A (if does not dropout within 0.1 sec).
Instantaneous setpoint 24A
During these two monitored starts the motor did not trip. However the peak of the bursts of current do exceed the peak value of the instantaneous setpoint (35*1.41), although apparently not long enough to cause a trip in this case. Also it seems plausible we may have been close to tripping the high dropout.