I have run across a couple of instances where ground fault relays trip when induction motors are starting.
For example, a 75hp, 480V, 3ph motor (113 FLA) would trip the main breaker on a ground fault condition during startup. The ground fault trip level was set at 160 Amps.
We raised the trip level to 320 Amps and the breaker no longer tripped.
In another instance, a 500hp, 480V, 3ph (approx 600FLA) motor would trip on ground fault when the ground fault was set below 400A.
Is there an acceptable level of ground fault current to expect when an induction motor starts?
For example, a 75hp, 480V, 3ph motor (113 FLA) would trip the main breaker on a ground fault condition during startup. The ground fault trip level was set at 160 Amps.
We raised the trip level to 320 Amps and the breaker no longer tripped.
In another instance, a 500hp, 480V, 3ph (approx 600FLA) motor would trip on ground fault when the ground fault was set below 400A.
Is there an acceptable level of ground fault current to expect when an induction motor starts?