reactive
Electrical
- Jul 9, 2002
- 54
Some comments from those of you with experience on gensets would be appreciated.
Client has bought an AVK diesel generator with the following ratings:
6,6kV
5300kVA @ pf 0,83
1500rpm
Unfortunately I do not have any further detail at this stage as the whereabouts of the manuals are a mystery.
Based on the above limited data is it possible to determine whether the gen will start a 1650kW synchronous motor DOL (also do not have much detail at this stage)?
While I can see that the gen kVA (current) rating would be exceeded for a short time the real power requirement should be OK.
Also, what would be the effect of regeneration from the motor (part of a Ward Leonard minewinder set) if the winder was the only load connected to the generator.
Client has bought an AVK diesel generator with the following ratings:
6,6kV
5300kVA @ pf 0,83
1500rpm
Unfortunately I do not have any further detail at this stage as the whereabouts of the manuals are a mystery.
Based on the above limited data is it possible to determine whether the gen will start a 1650kW synchronous motor DOL (also do not have much detail at this stage)?
While I can see that the gen kVA (current) rating would be exceeded for a short time the real power requirement should be OK.
Also, what would be the effect of regeneration from the motor (part of a Ward Leonard minewinder set) if the winder was the only load connected to the generator.