hbendillo
Electrical
- Jan 24, 2003
- 88
Here is the set up:
Medical duplex vacuum pump (alternting 10 HP motors) fed at 480-volt three-phase. Circuit parameters are 3-#8 & #10 G., 30-amp molded case circuit breaker. The pump is located in a boiler room which of course gets hot but we have not determined how hot. They only measured the temperature in their once and it was 104 F. The distance of the vacuum pump from the electrical source in terms of wiring length is no more than 320' but probably only about 300'. This pump is being fed from a panelboard that is on a separate service than is serving this part of the hospital. The service in question was for an addition to the existing building.
Motors and starters are burning up. Have replaced both motors and both starters. It appears the terminals on the starters are getting very hot. The circuit breaker has never tripped as far as we know and apparently the overloads in the starters are not taking the motors out. I don't see an severe arching within the control panel but when I looked at it the old starters had already been removed. A little plastic wiring tray for control wires that run in the control panel has a part that is melted and this part is right under one of the starters. Sounds like some kind of ground fault condition. The voltage on the circuit has been measured and is reading about 485 I think.
Any thoughts about what is happening. When the owner gets the unit up and running I am going to get him to install a meter to mearure and record voltage and amperage. But I don't want to burn up another motor or starters if I can help it. Thanks for the input.
Medical duplex vacuum pump (alternting 10 HP motors) fed at 480-volt three-phase. Circuit parameters are 3-#8 & #10 G., 30-amp molded case circuit breaker. The pump is located in a boiler room which of course gets hot but we have not determined how hot. They only measured the temperature in their once and it was 104 F. The distance of the vacuum pump from the electrical source in terms of wiring length is no more than 320' but probably only about 300'. This pump is being fed from a panelboard that is on a separate service than is serving this part of the hospital. The service in question was for an addition to the existing building.
Motors and starters are burning up. Have replaced both motors and both starters. It appears the terminals on the starters are getting very hot. The circuit breaker has never tripped as far as we know and apparently the overloads in the starters are not taking the motors out. I don't see an severe arching within the control panel but when I looked at it the old starters had already been removed. A little plastic wiring tray for control wires that run in the control panel has a part that is melted and this part is right under one of the starters. Sounds like some kind of ground fault condition. The voltage on the circuit has been measured and is reading about 485 I think.
Any thoughts about what is happening. When the owner gets the unit up and running I am going to get him to install a meter to mearure and record voltage and amperage. But I don't want to burn up another motor or starters if I can help it. Thanks for the input.