fieldserveng
Electrical
- Jan 28, 2005
- 6
Here's one for you. I am curious about the use of an MOV in parallel with a set of relay contacts as a form of arc suppresion for inductive loads. I have just discovered that the controller being used in an application is utilizing the arraingment that I have just mentioned. The MOVs are soldered onto the controllers mother board and are in parallel with the digital output relay's contacts. My understanding about MOVs is that their failure mode is to short circuit. I theorize that if the MOV fails and fails shorted the device being driven by this digital output will not be de-energized when commanded. In the application the manufacter is using a pre-packaged RC network in parallel with the inductive loads (interposing relay coils and some solenoids). The manufacter claims that in several thousand units they have never encountered the failure mode that I have a concern about.
Isn't this backwards? Wouldn't one specify an RC network in parallel with the relay contacts and a MOV across the inductive load?
Isn't this backwards? Wouldn't one specify an RC network in parallel with the relay contacts and a MOV across the inductive load?