Suction available to fire pumps always get my attention.
You're definitely going to want to confer with your insurance people.
"Also the requirements are 750gpm with 250gpm hose"
With careful design, and assuming the roof isn't steeply pitched, I would estimate the interior sprinker demand wil end up being between 780 gpm and 850 gpm which would give us between 1,030 and 1,100 gpm if we include hose stream.
I can see a potential problem using a 1,000 gpm pump and a definite problem if an RPZ is installed upstream the fire pump.
You are going to have 300 feet of equivalent loss even if you build the pump house adjacent to the city water main. An elbow, 20 feet of pipe and a tapping valve and sleeve will get you to 300 feet.
At 150% we need 1,500 gpm and at 1,500 gpm we are going to have 31 psi available at the pump suction flange. If we have the backflow preventor upstream the pump, with a loss of 16 psi, we're going to draw our suction down to 17 psi.
I would look at using a 750 gpm pump. You are not going to save any money with a 750, actually with larger overhead pipe you will probably be spending more, but the water supply should be able to easily provide 1,125 gpm while maintaining the suction above 20 psi.
Even with hose with careful design total demand for sprinkler and hose might be able to be limited not to exceed 140% of pump capacity.
I guess I am more sensitive then most on the issue of pump suction conditions. I come from Ohio and in most areas, including any test where the state fire marshal is involved, the state EPA requires a minimum 20 psi suction pressure be maintained at the pump suction or you fail the test. Couple this with the state fire marhsal having held intense classes on testing fire pumps, the inspector's know exactly what is needed and where to look, you can see how problems will develope.
I heard of one test where the pump suction drew down to 18 psi, the fire marshal called the test a failure and walked off. Could be very messy.
Will there be hydrants downstream the fire pump? If not the fire pump need only supply sprinklers in which case a 750 gpm pump would work very nicely.