Multi-battery design

Status
Not open for further replies.

lozano2

Industrial
Jul 16, 2008
18
Hi

I need to load banks of batteries OPZS (850 Ah c100) with one diesel generator of 60 kW.

The time of load foreseen is 6 hours a day.

Can someone recommend to me the most suitable system of load?

Thanks
 
Replies continue below

Recommended for you

A generator and chargers of batteries.

Thank you
 
The aim is to take advantage of a power not used in the generator to load batteries.

The problem is that it is a lot of power the generated one. We would need banks of batteries and a suitable system of load.

This it is the problem.

I do not know if the problem is understood well

Thanks
 
I'm not sure why you selected your batteries prior to designing the system.

While not specifically suitable, a UPS has the architecture that you desire:

Just bear in mind that a UPS is typically specified for 10 minutes of operation at full capacity, so you'd still need the equivalent of 36 30kW UPS systems to store a my assumed 50% excess, which you have not specified. I would suggest that you contact someone and have them configure a customized installation.

TTFN

FAQ731-376