Multi cable transit (MCT) system

Status
Not open for further replies.

NickParker

Electrical
Sep 1, 2017
421
Does NEC/Saudi Aramco permits the passing of both the power and control/Instrumentation cables through the same MCT?
 
Replies continue below

Recommended for you

It's permissible in maritime applications and per the NEC, but with Saudi Aramco, who knows?


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 
The MCT system it is a kind of fire stop using plugs of chloroprene [neoprene] fitted on a cable diameter and introduced in a metallic frame. Usually it is mounted on a wall opening where a channel continues from a side to another of the wall. The cable could be supported by a cable tray or running directly on the channel floor.
NEC permits cable of 1000 V or less to occupy the same cable raceway if the insulation is the same.[see art.300.3] So control cable could occupy the same raceway with power cables[usually]. Instrument cable only as permitted on 725 and 727 articles. See-for instance:
 