I am currently involved in the installation of the above, and have an major issue with the combined operation of these. Any advice on the details below would be greatly appreciated.
On site we have installed 3 new cooling towers, and 2 new chillers and one exisiting chiller. At present both suppliers are pointing fingers at one another, which leaves me in the middle trying to resolve why they do not work together.
The design conditions are 35.1 deg and 29.4 deg for the condensing water and 11.6 and 5.6 deg for the chilled. At present we are only running with a 2 - 3 deg split on the condensing water side (where the problem lies). The two new chillers are operating with their safety locks on and only at 66% and 80% capacity (one screw and one centfif. chiller). The main chiller is the centrif. which will go into overload prtection (high oil pressure - cond. water temp) when this approches 35 deg - never reaching, at patial load.
This leads me to believe the cooling towers aren't given the opportunity to work fully - am I correct?
I also understand the fundimentals of heat exchangers, and LMTD, but have been advised cooling towers do not operate in the same way - is this correct - if so what is their basis of heat rejection?
Why would the chiller cut out near design conditions - assuming this chiller is the correct one of course?
If any one has any ideas on what I should look for, or answers to the above I would be very greatfull.
On site we have installed 3 new cooling towers, and 2 new chillers and one exisiting chiller. At present both suppliers are pointing fingers at one another, which leaves me in the middle trying to resolve why they do not work together.
The design conditions are 35.1 deg and 29.4 deg for the condensing water and 11.6 and 5.6 deg for the chilled. At present we are only running with a 2 - 3 deg split on the condensing water side (where the problem lies). The two new chillers are operating with their safety locks on and only at 66% and 80% capacity (one screw and one centfif. chiller). The main chiller is the centrif. which will go into overload prtection (high oil pressure - cond. water temp) when this approches 35 deg - never reaching, at patial load.
This leads me to believe the cooling towers aren't given the opportunity to work fully - am I correct?
I also understand the fundimentals of heat exchangers, and LMTD, but have been advised cooling towers do not operate in the same way - is this correct - if so what is their basis of heat rejection?
Why would the chiller cut out near design conditions - assuming this chiller is the correct one of course?
If any one has any ideas on what I should look for, or answers to the above I would be very greatfull.