Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Multilin 750 Logic

Status
Not open for further replies.

cherry2000

Electrical
Jun 21, 2007
99
We have seperate Transformer Mechanical Alarms being hard wired to Logic Inputs in SR 750 relay (Logic Input 3 through Logic Input 7). See attachment.
We want to develop an "OR" logic within SR 750, so that in the event of any of these Mechanical Alarms going high, a common target relay needs to go high. We then want to read the status of this common relay as "Transformer Common Trouble" in Modbus ( RS485 link has alrady been established between DCS & the relays ).
Is it possible to do this? If yes, how....
 
Replies continue below

Recommended for you

Outputs 3 through 7 are auxiliary outputs that can be programmed operate from any of the user inputs, I believe. Refer to the relay manual.

You'll probably have to take care of the name of the alarm on the other end of the Modbus cable. I suspect you may be able to re-map the Modbus register to a user register as well.

The 750 is getting a bit long in the tooth and has fairly limited configuration/programming options compared with present generation protective relays.



 
Status
Not open for further replies.

Part and Inventory Search

Sponsor