Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Multilin GE SR 760 Relay Protection Element Tolerances

Status
Not open for further replies.

Joshua_Mc

Electrical
Oct 19, 2020
12
0
0
AU
Hi,

I was looking at the technical manual for the Multilin GE SR 760 Relay and I was trying to find the protection element tolerances - however, the level accuracy was only given as 'Per current input (I2 is 3 x input error)'. Can someone explain what this means?

Thanks in advance.
 
Replies continue below

Recommended for you

A relay doesn't measure I2, it calculates it from Ia Ib and Ic (each with their own tolerances)

So the I2 "measurement" has three lots of tolerances when compared to each of the phases.

This is my best guess as to what that probably means.
 
Status
Not open for further replies.
Back
Top